Tim Posted March 20, 2021 Share Posted March 20, 2021 Help-Where can I get the right breakers for my 48v set up ordered 2 from eBay they look kind of stinky dink .they are resetable the post looks like about 1/4 inch but metric of course.they have 2 screw holes to mount them.messed up .i went back and only see 12-24v .what am I missing looked at a coupe solar companies even worse.i know their out there .you guys bought yours somewhere.can you help? Quote Link to comment Share on other sites More sharing options...
Sid Genetry Solar Posted March 20, 2021 Share Posted March 20, 2021 What amperage are you looking for? Yes, the vast majority of "DC" breakers on eBay/Amazon are horrible quality Chinese junk units with fake ratings, etc. I wouldn't touch them with a 39.5' pole...a high-amperage DC arc is something you do NOT want to play with. Check YouTube for videos of improperly rated (or reverse-biased) DC breakers catching fire--it's not funny. I like to dig around eBay for used/new old stock Airpax magnetic trip breakers. The advantage of magnetic trip over heat-trip is...well...they aren't affected by heat, and often trip much faster. Most of the DC-rated ones are rated at 80vDC, 10kAIC (10,000A interrupt current), and often have a "sense switch" that you can use to detect if the breaker is tripped. If you're looking for >250A, search for GJ1P-series breakers (sort by price, haha, they're expensive brand new!) Should be able to nab a good, solid breaker for < $40/ea. (These are the huge ones that Sean has.) If you're looking for <150A, search eBay for "Airpax DC breaker." (I'm seeing 20A through 150A on a casual search.) KEEP IN MIND: Most of these are removed from old equipment...READ THE SPECIFICATIONS BEFORE BUYING! Make sure they're 80vDC rated. Sellers don't always advertise them right--or understand what they're selling. You should be able to get what you want for < $25/ea. (All of my breakers are this size/style. I have 5 10A, 1 each 40A, 90A, 150A.) There are other breaker brands besides Airpax out there (I have one Heinemann 40A DC breaker); if you want to search for "DC breaker" and weed out the 15,381 results of resellers marketing Chinese garbage...you likely will find some pretty decent breakers for a good price. But it'll take some time. As an example, here's a link to an Airpax breaker that the seller didn't include much info on. If this is the size you want, you can probably get a better price than a seller who knows what they're selling: https://www.ebay.com/itm/AIRPAX-LELHPK11-1RS4-30452-80-V-Circuit-Breaker-80V/274720081826 I looked at it, and noticed that it has as 50,000AIC rating--which is really good. Amperage isn't listed on the nameplate, and they don't show the toggle...but from the "Trip Amps" and the part number, I can infer that it's probably an 80A breaker. (Trying to find the manufacturer spec sheet also can be very handy...though most of these will have custom options that aren't in a manufacturer spec sheet). Another thing to keep in mind with most of these magnetic DC breakers...POLARITY IS IMPORTANT. The terminals are usually marked with text on the label closest to the terminal, you're looking for "LINE" and "LOAD." Line goes to battery positive, Load to the...well...load 😉 One other thing you might want to check is the "Delay" rating. A magnetic trip breaker with no delay will trip instantly upon a surge...so they usually use some fluid in the "trip mechanism" (often called "hydraulic magnetic trip") to slow the response down. There can be several different kinds of trip curves as a result...but for practical purposes, this usually can be ignored. 1 Quote Link to comment Share on other sites More sharing options...
Waterman Posted March 20, 2021 Share Posted March 20, 2021 DC breakers can also be marked as Bat and Aux as are the ones made by Bussmann. Some are only rated for 42Volts which is fine on a 24 Volt system while others are rated at 48 Volts. Quote Link to comment Share on other sites More sharing options...
TheButcher Posted March 20, 2021 Share Posted March 20, 2021 (edited) For what it's worth, I've been able to successfully break a shorted HV string of panels using TOMZN DC MCBs and confirmed that it wasn't a fluke by sacrificing one on the altar of testing by reversing the current and causing immediate failure and destruction of one. In terms of current, apart from dropping a lead acid bank across one in a similar test I have no way of actually testing the current handling ability and certainly no way of testing their claimed 6000A+ break rating. TOMZN's DC MCBs all seem to be C curve, which means instant trip via the magentic side of it needs > 5 times their rated current. I have seen the trip time curves vs ambient temperature & current graphs floating around the internet but again no way practical way to validate what they say. Edited March 20, 2021 by TheButcher added more info Quote Link to comment Share on other sites More sharing options...
Sid Genetry Solar Posted March 20, 2021 Share Posted March 20, 2021 11 minutes ago, TheButcher said: For what it's worth, I've been able to successfully break a shorted HV string of panels using TOMZN DC MCBs and confirmed that it wasn't a fluke by sacrificing one on the altar of testing by reversing the current and causing immediate failure and destruction of one. In terms of current, apart from dropping a lead acid bank across one in a similar test I have no way of actually testing the current handling ability and certainly no way of testing their claimed 6000A+ break rating. That's very good to know, as I have tandem TOMZN MCBs on all my solar arrays...they advertise 400vDC ratings, and I'm not sure whether to take that at face value or with some salt. Did find a YouTube video showing that even those breakers are getting "scam treatment", though they're reportedly easy to identify by a very low weight. 1 Quote Link to comment Share on other sites More sharing options...
TheButcher Posted March 20, 2021 Share Posted March 20, 2021 Yes, I saw BigClive's clip. Nothing surprises me these days when it comes to stuff coming out of China. The fakers even fake lead acid batteries by putting dead weight in the bottom of the case, which can't be that much less than the cost of making a genuine battery but they still do it. I purchase the breakers direct from TOMZN via Aliexpress, so hopefully the genuine articles make it to me (so far, so good). 1 Quote Link to comment Share on other sites More sharing options...
Carlos Posted March 21, 2021 Share Posted March 21, 2021 Tomzn are fine. In Europe they use a lot of them. As long as you order from the official Tomzn store you will get the real breakers. You can also use the magnetic hydraulic (black color breakers) from midnite or bluesea but they are very expensive compared to the Tomzn. 1 Quote Link to comment Share on other sites More sharing options...
wpg205 Posted March 22, 2021 Share Posted March 22, 2021 Just to chime in - there are also alot of nonpolarized DC breakers. Midnight solar sells alot of both (would like to hear what @Sid Genetry Solar thinks) but here is a link to their product offerings. I have a question though. Say I want to totally disconnect my panels from the SCC and I need to use polarized breakers. Typically breakers have a (+) sign, where the higher potential voltage is supposed to enter. How I would use this breaker on the positive wire is straightforward - the positive from the PVs enters the (+) side of the breaker. But what about when I want to add a polarized breaker to the negative wire? Should it be reversed, with the wire coming from the SCC entering the positive side of the breaker? I've got an array which, when paralleled, will be up to 90 volts and 60 amps, and I was hoping to figure out the cheapest, safes and easiest way to fully disconnect and protect it when I need to. I have each individual string fused on the positive wire. Quote Link to comment Share on other sites More sharing options...
TheButcher Posted March 22, 2021 Share Posted March 22, 2021 (edited) My two cents of advice is that you should contact the breaker manufacturer or check the product datasheet to ensure you wire it the right way or be prepared to do your own polarity tests and possibly write off the breaker in the process. The magnet orientation is the critical part as it has to push any arc towards the trap. If the current is flowing the wrong way in relation to the magnet and the other side of the ganged breaker also flows the wrong way the arc will be push back into the contact area rather than the trap on both sides and fires ensue. If you can rely on the breaker simply being two identical single breakers being ganged and want to break the + and - wires you would normally place both the array wires on the + sides of the breaker. That way the current flows through one breaker in the wrong way, ensuring that regardless of wiring errors or even a fault where power can flow back into the array, the current can be interrupted. Edited March 22, 2021 by TheButcher checking forum tags Quote Link to comment Share on other sites More sharing options...
Waterman Posted March 22, 2021 Share Posted March 22, 2021 2 hours ago, TheButcher said: My two cents of advice is that you should contact the breaker manufacturer or check the product datasheet to ensure you wire it the right way or be prepared to do your own polarity tests and possibly write off the breaker in the process. The magnet orientation is the critical part as it has to push any arc towards the trap. If the current is flowing the wrong way in relation to the magnet and the other side of the ganged breaker also flows the wrong way the arc will be push back into the contact area rather than the trap on both sides and fires ensue. If you can rely on the breaker simply being two identical single breakers being ganged and want to break the + and - wires you would normally place both the array wires on the + sides of the breaker. That way the current flows through one breaker in the wrong way, ensuring that regardless of wiring errors or even a fault where power can flow back into the array, the current can be interrupted. Some are even marked that way from the factory when you get them in 2 pole versions with a common trip. Eaton/Moeller breakers as an example are marked that way. The left one is marked + on the top and - on the bottom while the right one is marked - on the top and + on the bottom. Quote Link to comment Share on other sites More sharing options...
TheButcher Posted March 22, 2021 Share Posted March 22, 2021 Here's the confusing part. If you put the most positive wires on the + terminals of that breaker, and then follow the current flow through it, is that causing reverse flow through one side so that regardless of current flow direction at the time of the breaker opening any arc pulled will 100% be forced into the trap on one side ensuring successful break of the current? ie, one side has the + and - labelling reversed in relation to the arc magnet Some breakers have the + on both breakers at the bottom, and some reversed like this. Unless you understand how the magnets are set up you can't be sure it will function properly. That's why I advise people to check the manufacturer's information about how to wire them up. Quote Link to comment Share on other sites More sharing options...
Sid Genetry Solar Posted March 22, 2021 Share Posted March 22, 2021 5 hours ago, wpg205 said: I have a question though. Say I want to totally disconnect my panels from the SCC and I need to use polarized breakers. Typically breakers have a (+) sign, where the higher potential voltage is supposed to enter. How I would use this breaker on the positive wire is straightforward - the positive from the PVs enters the (+) side of the breaker. But what about when I want to add a polarized breaker to the negative wire? Should it be reversed, with the wire coming from the SCC entering the positive side of the breaker? That would be my hunch. Uneducated country bumpkin opinion 😉 Also worth noting that polarized breakers on the battery side of SCCs (solar charge controllers) are quite an interesting conundrum. It could be argued that breaker positive goes to the SCC positive (breaker negative to the battery positive terminal), as that's the way power normally flows through it. But there's an issue: the one and only way that an SCC battery breaker can trip (if properly sized!)--is if the SCC internally fails and shorts out the battery through it's FETs. Suddenly the tables are turned, and the breaker must break the full battery voltage (and current!) the other way. Interestingly enough, if a power supply has an electrolytic capacitor on it close to where you short the wires out, it is pretty nigh impossible to pull a DC arc. SCCs inevitably have a fair amount of filtration right at the battery terminals...so breaker polarity may not matter as much in this case. With that in mind, I do have the SCC battery breakers on my system mounted breaker positive to battery positive. Have had an MPPT blowup trip the battery breaker. (And because I tandemed the solar input and battery breakers together, this also disconnected solar from the MPPT, so it had zero power potential on it.) One of those mysterious blowups--I was tweaking the charge voltage configurations on a Morningstar Tristar TS-MPPT-60. Had done it 4-5 times already (still not accepting the settings because I hadn't set the DIP switches right)...and the final time, after updating the appropriate setting registers, I sent the MODBUS Restart command (like before)...it restarted, did the power-up sequence...followed by a deep "pop" and simultaneous bright orange flash--tripping the breakers. Fortunately, Morningstar replaced it under warranty...and very quickly at that. To this day, I'm scared to touch the charge settings in the replacement unit...37,000 hours on it so far. Quote Link to comment Share on other sites More sharing options...
Waterman Posted March 22, 2021 Share Posted March 22, 2021 (edited) 37 minutes ago, TheButcher said: Here's the confusing part. If you put the most positive wires on the + terminals of that breaker, and then follow the current flow through it, is that causing reverse flow through one side so that regardless of current flow direction at the time of the breaker opening any arc pulled will 100% be forced into the trap on one side ensuring successful break of the current? ie, one side has the + and - labelling reversed in relation to the arc magnet Some breakers have the + on both breakers at the bottom, and some reversed like this. Unless you understand how the magnets are set up you can't be sure it will function properly. That's why I advise people to check the manufacturer's information about how to wire them up. It would be interesting to cut them open to find out. The Kayal brand is also marked that way. Eaton branded ones are marked as 48/60VDC and 277/480VAC on some FAZ-NA models. Reason they may be able to get away with either direction is that they are both magnetic and thermal. Edited March 22, 2021 by Waterman Quote Link to comment Share on other sites More sharing options...
TheButcher Posted March 22, 2021 Share Posted March 22, 2021 Feeling around with a small bar magnet is usually enough to tell you which way the magnet is oriented then check on the other side of the set to see the 2nd one is facing the same direction. I'd still check with the manufacturer, checking is only confirmation of what the manufacturer says IMO rather than the only check. Quote Link to comment Share on other sites More sharing options...
TheButcher Posted March 22, 2021 Share Posted March 22, 2021 1 hour ago, Sid Genetry Solar said: Interestingly enough, if a power supply has an electrolytic capacitor on it close to where you short the wires out, it is pretty nigh impossible to pull a DC arc. SCCs inevitably have a fair amount of filtration right at the battery terminals...so breaker polarity may not matter as much in this case. With that in mind, I do have the SCC battery breakers on my system mounted breaker positive to battery positive. The regs here say thou shalt fit a non-polarised breaker but I think that is really more directed at transformerless grid tied inverters where there is a potential (tickets still on sale, I'm here all week) for rectified mains voltages to appear on the panel wiring so any breaker must be able to handle current in and out of the array. Quote Link to comment Share on other sites More sharing options...
TheButcher Posted March 22, 2021 Share Posted March 22, 2021 I did a little digging, the requirement for a non-polarised ganged breaker here is partly due to the mains risk in transformerless inverters, but also partly because of clown installers using incorrectly wired single polarised breakers causing fires. Quote Link to comment Share on other sites More sharing options...
wpg205 Posted March 23, 2021 Share Posted March 23, 2021 (edited) Thanks for the thoughts/suggestions. Anyone have have a suggestion for a polarized or non-polarized 2 pole DC breaker that they trust? I'll have max amps of 60 and volts 100<. I've searched and searched and haven't quite found anything. I need it to be din mounted. Edited March 23, 2021 by wpg205 Quote Link to comment Share on other sites More sharing options...
TheButcher Posted March 23, 2021 Share Posted March 23, 2021 I'd be happy with a 2 pole TOMZN. They have a range of options, but here's a 2 pole 80A 600VDC rated one. If you contact them they can supply the datasheet and wiring arrangements for their breakers. https://www.aliexpress.com/item/32788927432.html?spm=2114.12010612.8148356.19.29f1a4c5Vrrdda Quote Link to comment Share on other sites More sharing options...
TheButcher Posted August 20, 2021 Share Posted August 20, 2021 Well, now not so happy. The Tomzn breakers do work well but I just discovered something that isn't so good. For no particular reason I had the box of spare breakers on my bench and idle curiousity got the better of me so I started checking the magnet orientation in them. 1 of them was reversed. Nice. Effectively it means that if this breaker was wired with source and drain on the same side as the others, the contacts opened and a persistent arc formed (not always the case) it would be pulled down into the contacts (or pushed into, I don't know the internal layout) instead of being forced into the arc trap and extinguished. I will be checking all the ones in service later today. It always pay to test stuff purchased from China, even if it is a reputable brand. Quote Link to comment Share on other sites More sharing options...
Sid Genetry Solar Posted August 20, 2021 Share Posted August 20, 2021 Is this a single-pole breaker? I'm aware that the 2-pole breakers seem to have the polarities reversed between the 2 poles. Quote Link to comment Share on other sites More sharing options...
TheButcher Posted August 21, 2021 Share Posted August 21, 2021 Yes, single pole. The 2 pole breakers are reversed with the intended wiring to ensure one side is always going to push any arc into the trap and break the circuit. I'll still use Tomzn breakers, they seem pretty robust, but from now on I will be checking the magnet orientation in singles to ensure its the right way around and in 2 poles to ensure they are opposed orientation. 1 Quote Link to comment Share on other sites More sharing options...
TheButcher Posted August 21, 2021 Share Posted August 21, 2021 I forgot to mention, my use methodology is: if the thing on the far side of the breaker can only ever sink current I am happy to use a single pole breaker If the thing can both source and sink, ie a battery or a charger (defect = draws current), I use a 2 pole breaker since it has to be able to safely break current flows in both directions. Quote Link to comment Share on other sites More sharing options...
TheButcher Posted January 10, 2022 Share Posted January 10, 2022 On 8/21/2021 at 12:26 PM, TheButcher said: I'll still use Tomzn breakers, they seem pretty robust, but from now on I will be checking the magnet orientation in singles to ensure its the right way around and in 2 poles to ensure they are opposed orientation. My opinion is changing. The Tomzn breakers I have are supposedly 125A. Today I put one to the test. Standard conditions would have these things tested at 25c air temp but being summer here it's 31c instead. Not that significant in the scheme of things but even so it has to be considered. The breaker was in free air, no obstructions on either side nor any other heat sources such as another hot breaker and all cabling / fittings in good stead. With my inverter chugging along at 2800W AC ouput, meaning DC amps should be around 125A (24V lifepo4, bus voltage was nigh on 25, 90%-ish efficiency in the inverter) and found acceptably close via a DC clamp meter. The breaker held on for a few minutes then tripped. Well it's better to have a breaker let go early than late but it should have kept going for a lot longer in ambient 31c, a lot longer. Unfortunately that's not the end of it. The breaker, given plenty of time to cool, will not reset. It's toast. I think I'll try some TAIXI MCCBs and see how they go. Stay tuned. Quote Link to comment Share on other sites More sharing options...
Sid Genetry Solar Posted January 10, 2022 Share Posted January 10, 2022 23 minutes ago, TheButcher said: The breaker, given plenty of time to cool, will not reset. It's toast. Very interesting. I've got several of these breakers on the MPPT charge controllers--but all the main power breakers I'm using are non-Chinese units (i.e. Airpax, Heinemann, etc.) Worth noting that I've even had problems with (used) GJ1P breakers tripping early AND half-tripping (i.e. only one pole tripping, but not both)--context being the 12kw inverter tests at Sean's w/ a 300A GJ1P. I will be very interested to hear how some "TAIXI" breakers handle. They're all so similar in design (except for the print) that I can't help but wonder if they're all just rebrands of the same shoddy breaker manufacturer... 1 Quote Link to comment Share on other sites More sharing options...
InPhase Posted January 10, 2022 Share Posted January 10, 2022 I know that budget can be a concern, but when it comes to circuit breakers handling any appreciable current, I stick to known quality manufacturers. The ones you would use for line voltage distribution, like Eaton or Schneider/Square D, Siemens, or even, God help me, GE. There are some pretty decent used ones. A large frame enclosed circuit breaker from nearly any manufacturer will have a DC rating. Sometimes you have to use a two or three pole breaker with the poles in series to get that rating, but that, in my opinion, is better than chancing it with a Qong Poo Best Electrics, Ltd. brand breaker. 1 Quote Link to comment Share on other sites More sharing options...