 the daly bms isnt really big enought to handle my discharge load and since im using a seperate heltec balancer because of dalys poor balancing capabilities im wondering if i couldnt just use a anl fuse for overload protection and maybe some form of disconect being that the gs inverter has a low voltage shut off ?

 

 

 

 

Link to comment
Share on other sites

1 hour ago, Sid Genetry Solar said:

It probably doesn't like surge loads from the inverter, right?

Or could you be more specific as to what the issue is?  (I know their balancing is pretty much useless on anything larger than R/C equipment batteries!)

the daly bms isnt really big enought to handle my discharge load and since im using a seperate heltec balancer because of dalys poor balancing capabilities im wondering if i couldnt just use a anl fuse for overload protection and maybe some form of disconect being that the gs inverter has a low voltage shut off ?

Link to comment
Share on other sites

24 minutes ago, Bobby T said:

the daly bms isnt really big enought to handle my discharge load and since im using a seperate heltec balancer because of dalys poor balancing capabilities im wondering if i couldnt just use a anl fuse for overload protection and maybe some form of disconect being that the gs inverter has a low voltage shut off ?

That is what I would personally do.  Instead of an ANL fuse, I'd suggest a properly rated DC-rated breaker (200A should be sufficient), as if for whatever reason it trips, you don't have to buy new fuses!  And if you need to disconnect power to the inverter, just flip the breaker off--no tools required.  You can search eBay for GJ1 or GJ1P; those used breakers can often be found for a pretty good price.  They are usually rated to 80vDC, which is sufficient for a 48v nominal system.

As long as the batteries are well balanced (and not regularly being deep-cycled), a properly set low voltage shutoff on the inverter should be decently sufficient safety.  I personally don't have a "BMS" on my house LiFePo4 battery bank.  As long as you know what you're doing, and are aware of the battery limits, you should be fine with a breaker and inverter configuration.

Link to comment
Share on other sites

Ah, 24v...200A is way too low to run serious loads there!  You'd need a 400A disconnect for continuous full load operation on the inverter.

Worth noting that most AC rated breakers are DC rated to 32vDC--so you could basically use any 300-400A breaker that you could find.

Also: do NOT use the cheap little breakers that have overrun eBay and Amazon like the flies:

image.png.13661d3de0b133bf3e1d985c95cd9755.png

These little pieces of junk are pretty well guaranteed to trip far sooner than expected--or even not at all.  They probably would make your Daly look good by comparison.

 

So for mathematical purposes, 6,000W * 1.1 (90% efficiency) = 6,600W input load / 24v = 275A RMS at full load. 

Note that a thermal breaker will trip by RMS current; a magnetic breaker seems to trip by peak current.  To calculate peak current, take the 275A RMS * 1.414 (square root of 2) to get the peak amperage = ~390A peak.  So a 300A thermal breaker, or a 400A magnetic breaker should be sufficient.

...yeah, that's a lot of amps at 24v!

Link to comment
Share on other sites

40kwh of LiFePO4... wow.
I got 10kwh. Eventually i'd like 30kwh... basically 72 hours of normal power use...

I did now know you could use any [basically] AC breaker for 24v... I've been using fuses instead. (never blown one, thankfully...)
A bit weird... would one use a double-pole breaker? Or single pole on positive?

Now i see some cleanup in my future...

Link to comment
Share on other sites

12 minutes ago, NotMario said:

I did now know you could use any [basically] AC breaker for 24v... I've been using fuses instead. (never blown one, thankfully...)
A bit weird... would one use a double-pole breaker? Or single pole on positive?

Whatever works.  Issue with higher DC voltages is the arc--which if the breaker isn't specifically designed to quench said arc, the breaker will literally start a fire when you trip it or turn it off.  But more often than not, an AC-rated breakers will have a 32vDC rating (when listed).  It could be safe to assume that an AC-rated breaker with no DC rating would also be safe for 32vDC.

You could use a double-pole breaker and double it up for double the amperage rating...maybe? 

I don't see any benefits to disconnecting DC negative honestly.  Risks of disconnecting DC negative would include "floating" equipment...or the worst being alternate unexpected ground paths (like RS-232 or USB cables) that aren't rated to carry significant current.  If one of those got blasted with power due to an open ground, you'd have fried cables and blown electronics very quickly!

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share

×
×
  • Create New...