Sean Genetry Solar Posted February 19, 2021 Share Posted February 19, 2021 Quote Link to comment Share on other sites More sharing options...
dochubert Posted February 20, 2021 Share Posted February 20, 2021 Hi Sean, That beast looks great! Do you know what the kva rating is for that transformer? Also, when you want to load test the inverter with heavy loads, you could switch your water heater to run on elements only. 4500-5000 watts? Plus your regular loads should do it. Quote Link to comment Share on other sites More sharing options...
Sid Genetry Solar Posted February 20, 2021 Share Posted February 20, 2021 11 hours ago, dochubert said: Do you know what the kva rating is for that transformer? Haha. I wrote the winding specification right here on my laptop...wire diameter, number of parallel strands, number of turns, location of the winding terminations...this is no "off-the-shelf transformer." It's 100% custom just for Genetry Solar, based on Genetry Solar specifications. The windings are design rated for 12kw continuous. The only unknown is the temperature rise from the core; that's what we'll determine when it's load tested. But as large as the core is, I do not expect this to be a problem. Quote Link to comment Share on other sites More sharing options...
dochubert Posted February 21, 2021 Share Posted February 21, 2021 That's great! Guess we don't have to worry about a "tiny L2 wire" on this one, eh? Quote Link to comment Share on other sites More sharing options...
Sid Genetry Solar Posted February 21, 2021 Share Posted February 21, 2021 13 minutes ago, dochubert said: That's great! Guess we don't have to worry about a "tiny L2 wire" on this one, eh? Absolutely. GS transformers are completely balanced, both in specification and output voltage. 1 Quote Link to comment Share on other sites More sharing options...
AquaticsLive Posted February 23, 2021 Share Posted February 23, 2021 Looking good, as it moves along all the items inside are made better or better options chosen than the original PJ parts. I am thinking that the relationship with Power Jack will be mutually beneficial. Quote Link to comment Share on other sites More sharing options...
Sid Genetry Solar Posted February 23, 2021 Share Posted February 23, 2021 44 minutes ago, AquaticsLive said: I am thinking that the relationship with Power Jack will be mutually beneficial. That is the goal. Not just on the balance sheet side of things, but to also improve their product as well. Quote Link to comment Share on other sites More sharing options...
The Blind Wolf Posted February 23, 2021 Share Posted February 23, 2021 Just was thinking Sid. Why can L1 and L2 be separet cores? Have them sideways instead of the normal way and have fans blowing directly through the cores. Seem like if l1 and l2 wasn't together it would help on the heat problems. and uhm, why round? couldn't it be square, or shape like a pillar. I might be missing something, is it cause of the magnetic field. Since far as I know there isn't a magnet in the center of these corils. Quote Link to comment Share on other sites More sharing options...
Sid Genetry Solar Posted February 23, 2021 Share Posted February 23, 2021 OK, transformer basics... The heat is generated by losses, of the core and the windings on the core. In the case of a stock PJ inverter, the windings are severely undersized, causing them to generate a huge amount of heat at high load. Separating this waste heat across 2 cores simply gives you more area to dissipate the heat, but it does not reduce the heat. If you separate the L1 and L2 secondary windings to separate cores, now you need two primary windings as well. If the windings and core are mathematically sized for this difference, the total wire and core cross section will remain the same--however, you've created twice as much work required to manufacture the inverter. And the heat problem will remain the same, due to the inadequate winding specification. Why is the transformer round? Most other low-frequency inverters use a square-frame transformer, characterized by (comparatively) very high idle currents, and reduced efficiency. The round toroidial transformer is difficult to mount, but it is significantly more efficient, with much lower idle current. I haven't studied this sort of thing to explain why, I just appreciate that it is ;-). You are correct, there is no "magnet" in the center of the toroid cores, however when they're running, there is an extremely strong magnetic field present in (and around) the cores due to the electromagnetic principle of wire wrapped around a magnetically permeable material. I personally mounted a "9kw" PJ AS-5 transformer sideways, with a 200CFM fan blowing directly through the center of the core. Still overloaded at a 3kw load. 1 Quote Link to comment Share on other sites More sharing options...
The Blind Wolf Posted February 23, 2021 Share Posted February 23, 2021 Thanks Sid for the lesson. I'm always learning new things. I got into this hobby about three years ago, and learning how things work from eletrical to makeing batteries. Kind of fun. Too bad you can't incorporate water cooling into a coil, sort of using a heat pipe design with prefilled water, seem you could make a thicker wire with water cooling and use less wire to get the same results. Quote Link to comment Share on other sites More sharing options...
Sid Genetry Solar Posted February 23, 2021 Share Posted February 23, 2021 30 minutes ago, The Blind Wolf said: Too bad you can't incorporate water cooling into a coil, sort of using a heat pipe design with prefilled water, seem you could make a thicker wire with water cooling and use less wire to get the same results. Not like hollow copper pipe hasn't been used before on huge transformers for just this reason ;-). Of course, by the time you need water cooling, there's significant losses involved...so it's easier just to calculate the winding specification to carry the desired load. Quote Link to comment Share on other sites More sharing options...
dochubert Posted February 24, 2021 Share Posted February 24, 2021 Quote I personally mounted a "9kw" PJ AS-5 transformer sideways, with a 200CFM fan blowing directly through the center of the core. Still overloaded at a 3kw load. There's got to be something wrong with that transformer! My old 3 transformer pj (3 AS2 xfmrs in parallel) can do 4-5kw for hours with good fan control. It'll do 6kw for a short while... Quote Link to comment Share on other sites More sharing options...
Sid Genetry Solar Posted February 24, 2021 Share Posted February 24, 2021 Sean said the same after I told him about it. Only thing I can guess is perhaps the core...but the windings were good. Actually took that one apart, paralleled all 3 tiny strands of wire (1 on one phase, 2 strands on the other) for one phase, added a whole winding for the second phase, and put the primary back on...don't recommend that to anyone for an afternoon project...but it seems to run cooler. It was designed before PJ started making transformers in-house, and had copper wire. A friend provided me a hand-wound transformer that runs like a dream in comparison...ever since installing it, my 200CFM fans have NEVER reached full speed. Come to think of it, they've never reached 50% speed, either... Would have to say that the 3 AS2s running 5kw is about 1.66kw each. As PJ can't run less than 1 strand of wire for a coil, that sounds about right. Quote Link to comment Share on other sites More sharing options...
Waterman Posted February 24, 2021 Share Posted February 24, 2021 2 hours ago, Sid Genetry Solar said: Sean said the same after I told him about it. Only thing I can guess is perhaps the core...but the windings were good. Actually took that one apart, paralleled all 3 tiny strands of wire (1 on one phase, 2 strands on the other) for one phase, added a whole winding for the second phase, and put the primary back on...don't recommend that to anyone for an afternoon project...but it seems to run cooler. It was designed before PJ started making transformers in-house, and had copper wire. A friend provided me a hand-wound transformer that runs like a dream in comparison...ever since installing it, my 200CFM fans have NEVER reached full speed. Come to think of it, they've never reached 50% speed, either... Would have to say that the 3 AS2s running 5kw is about 1.66kw each. As PJ can't run less than 1 strand of wire for a coil, that sounds about right. A lot of people down under and in England have been stripping toroidal transformers and rewinding them to get what they want. And they work. Sounds like your friend did the same for you. Quote Link to comment Share on other sites More sharing options...
Sid Genetry Solar Posted February 24, 2021 Share Posted February 24, 2021 Yeah, he's got the patience I don't 😇. After that minor rewinding job, I threw in the towel. It isn't easy work...you have to get the wire re-bent neatly in place, or there's no way to get enough wire 'round that core to get the desired output wattage. Quote Link to comment Share on other sites More sharing options...