pilgrimvalley Posted July 7, 2021 Share Posted July 7, 2021 a 3 piece stainless steel inverter. transformer in one box, control box is a second larger ss box and the 3rd ss small box is labeled thor's notebook and has the 2 lcd screens. i will send pictures later . the transformer box said asl 6.5 i believe. it came with a upower manual which does not correspond to this inverter in anyway. it was sold on ebay as a powerjack inverter but there is no place on the inverter that has any brand naming that i can see. trying to arrange 3 boxes in a tight space with interconnecting cable is the next challenge. got it unboxed with no external damage and inside my solar power shed before the rains started yesterday. also assembling a 32 cell 8S4P 1088ah LiFePO4 battery using 272Ah Lishen cells. i have some other LIFePo4 batteries i can test it on eventually after bit. needed the rain but definitely humid now. Quote Link to comment Share on other sites More sharing options...
pilgrimvalley Posted July 7, 2021 Author Share Posted July 7, 2021 previous powerjack inverters had genetry solar label on the included manual. this one does not. evidently they are hiding the powerjack name a bit now. no new manual as this is an old manual which does not correspond to this inverter much. Quote Link to comment Share on other sites More sharing options...
pilgrimvalley Posted July 7, 2021 Author Share Posted July 7, 2021 a couple pics. the transformer has one fan, the controller box has two fans, there are several cables to connect the boxes. it is not what i have seen before. cell phone pics are hard to get uplaoded on slow cell connection. more later. Quote Link to comment Share on other sites More sharing options...
pilgrimvalley Posted July 7, 2021 Author Share Posted July 7, 2021 2 more pics. Quote Link to comment Share on other sites More sharing options...
dickson Posted July 7, 2021 Share Posted July 7, 2021 i will send pictures later . the transformer box said asl 6.5 i believe I think the ASL6.5 is a good transformer because it is 30VAC to 240VAC and may run cooler . My 15kw Powerjack has a ASL9 transformer run 36VAC to 240VAC and get hot so I run at 61 vdc input . Yours maybe run at lower DC input . Powerjack doing a lot of changes . 1 Quote Link to comment Share on other sites More sharing options...
dickson Posted July 7, 2021 Share Posted July 7, 2021 Sorry yours is 24v input so it is not 30vac to 240vac but I think it will still run cooler with the ASL 6.5 . I do not think a ASL9 is in any 24v 15kw powerjack . 1 Quote Link to comment Share on other sites More sharing options...
pilgrimvalley Posted July 7, 2021 Author Share Posted July 7, 2021 Quote Link to comment Share on other sites More sharing options...
pilgrimvalley Posted July 7, 2021 Author Share Posted July 7, 2021 the above is how the website shows to interconnect the transformer and control board boxes. the transformer is on the bottom. the control box on top. thge Thor's notebook box with the 2 lcd screens is not shown but it likely hooks up in the other end of these 2 boxes. have not quite de-cyphered that part out yet. more later. Quote Link to comment Share on other sites More sharing options...
pilgrimvalley Posted July 7, 2021 Author Share Posted July 7, 2021 it says 11.1 so i think that is the control board version; and at 60 hz on the box. thor's note book has 2 of the round screw on type 7 pin lcd cables which are about 7 feet long to connent the lcd screens to the other end of the somehow? have to turn it around. it is a fairly heavy >>>> the transformer and control box but there is a note that says to connect the lcd screens before turning on the inverter to prevent burning out the lcd screens. so have to figure that end out also. Quote Link to comment Share on other sites More sharing options...
pilgrimvalley Posted July 7, 2021 Author Share Posted July 7, 2021 Quote Link to comment Share on other sites More sharing options...
pilgrimvalley Posted July 7, 2021 Author Share Posted July 7, 2021 have to look at web site for the connections a bit as they are not in the included manual. maybe Sid can make them a good manual! 😎 Quote Link to comment Share on other sites More sharing options...
pilgrimvalley Posted July 10, 2021 Author Share Posted July 10, 2021 our ac output as follows: 2 ac output socket, output is 110v, also we have hard wire terminal-----L1, N, L2, L1+L2=220V, L1+N=110V, L2+N=110V Note: can not L1+N+L2 at the same time!!! 15000W Low Frequency Split Phase Pure Sine Wave Power Inverter DC 24V AC 110V,220V 60HZ With UPS & ATS With 110V Battery Charger With 110V & 220V LCD Display Box AC 110V: 7500W continue power, 30000w peak power AC 220V: 7500W continue power, 30000w peak power We separte the control board and the transfomer in two boxes, so cusotmer will receive two boxes as photos show,one is the transformer box,the other is the control box Quote Link to comment Share on other sites More sharing options...
pilgrimvalley Posted July 10, 2021 Author Share Posted July 10, 2021 so u can only do either 7500 watts at 110 volt or 7500 watts at 220 volt? it says you can't do both at the same time what does that mean for wiring up a split phase inverter? Quote Link to comment Share on other sites More sharing options...
pilgrimvalley Posted July 10, 2021 Author Share Posted July 10, 2021 the original listing said it would do 15000 watts continuously the after buying they updated the listing to say 7500 watts continuos. 7500 would work for most anything i would be using i think. Quote Link to comment Share on other sites More sharing options...
Sid Genetry Solar Posted July 10, 2021 Share Posted July 10, 2021 @pilgrimvalleyFirstly, you bought a PJ inverter. Consider yourself very fortunate to be able to reach 1/2 of that rating continuously...with a more reasonable expected maximum sustained continuous output of 30%. Most "cheap" inverters utilize either deceptive ratings (i.e. advertising the peak)...or they will use simply fallacious numbers. I will note that for wiring up a PJ inverter...the L1 / N output circuit more often than not has twice the transformer wire than the L2 / N output circuit. But for practical purposes, this won't mean much. Quote Link to comment Share on other sites More sharing options...
Sid Genetry Solar Posted July 10, 2021 Share Posted July 10, 2021 1 hour ago, pilgrimvalley said: Note: can not L1+N+L2 at the same time!!! I suspect that this has to do with the input circuit, which for 220v input inverters must only consist of L1 / L2, and Neutral / ground-bonded neutral must never come CLOSE to the inverter. Quote Link to comment Share on other sites More sharing options...
dickson Posted July 10, 2021 Share Posted July 10, 2021 Note: can not L1+N+L2 at the same time!!! When I first connect my 15kw PJ to the main service L1 N L2 and it run the heat pump with no problem when the 120vac for the refrigerator and the freezer was not running . When the 120vac freezer and refrigerator is on at the same time as the 240vac heat pump is also on then L1 and L2 is way out of balance and the light flicker bad and I shut everything down . Now I directly connect the heat pump L1 L2 G and no problem with L1 L2 out of balance . The most I get is 6100 watts . I think your ASL 6.5 is a good transformer and will also run my heat pump directly wired L1 L2 G . PJ inverters has no surge protection . Thank for your information . Quote Link to comment Share on other sites More sharing options...
pilgrimvalley Posted July 12, 2021 Author Share Posted July 12, 2021 do you ever think that powerjack may read your responses. in previous videos i obseved a 1500 watt inverter running 2600 watts. but this is their newest style inverter 15000 watts and is said to do 7500 watts contiuosly. i will not be using their ac charging or ups. only the off-grid 24 volt inverter hooked to a 120/240 panel. their warranty is not very good but it seems they have upped their inverters a bit. i have several 24-volt 5kw LiFePO4 batteries i will test it on in a few days hopefully. i know they won't allow me to bid on auction after they had to replace the very heavy 20,000 watt inverter 48-volt lf sp psw that arrive to me as their 1st guineypig due to shipping damage; bad packaging. the powerjack seller names just change on ebay --- but still sold by powerjack. this inverter arrived in 3 separate boxes from california in good condition. no physical damage noted. i hope it does 7500 watts without any problems...time will tell! the 6000 and 8000 watt ss inverters have been running continuosly for months at low load though. expensive lights and coffee maker everyday and all night bug zapper. this is a lot larger inverter than the 6000 and also a lot larger than the 8000 watt sp psw lf inverter i currently am running. i ran heat lamps in the barn all winter at about 200 feet away also for the baby hair sheep. you know they had to be born december 21st. Quote Link to comment Share on other sites More sharing options...
dickson Posted July 12, 2021 Share Posted July 12, 2021 do you ever think that powerjack may read your responses. in previous videos i obseved a 1500 watt inverter running 2600 watts. but this is their newest style I think youtube is block in China but people in Walnut CA will read this forum and is making new style control board and LF driver and is selling ASL11 ASL10 ASL9 and ASL 6.5 transformer on ebay . UPS do their fast delivery in the US . I do not think ASL11 transformer can do more than 10kw continue at least I can not find any test in youtube . Me and you are guineypigs . Quote Link to comment Share on other sites More sharing options...
pilgrimvalley Posted July 12, 2021 Author Share Posted July 12, 2021 i wonder if they took business away from genetry solar due to the negative comments or negative reviews; which were more glowing sometimes on the early youtube videos? i am sure feedback goes back to china. when i complained and made a negative review they no longer allow me to bid on ebay. so they are a lot more shifty in teir ways of projecting their products. they chnge vedor names and change product names but still are powerjackproducts. no explanation just action reaction without explanation. if they read many negative comments, their reaction likely will not be positive. a company that has hundreds possibly thousands of employees working for pennies compared to what is paid in the USA. they do not advertise for genetry solar on their included manual anymore. just an observation. before sean talked of opening a retail store with them in his videos, but now the rhetoric goes back and forth. my 24-volt systems are running Electrodacu SBMS0 on LiFePO4 battery banks off grid. there is no incentive to give power to the grid in south dakota where these are set up. working toward a totally offgrid redundant system for the farm. Quote Link to comment Share on other sites More sharing options...
pilgrimvalley Posted July 12, 2021 Author Share Posted July 12, 2021 i have been acquiing more electric appliances to test and utilize the solar pv power via the offgrid inverters. coffee everday and pressure cookers, bug zappper, led lights, 24 volt water pumps, 24 volt water heater elements etc.table saws etc. Quote Link to comment Share on other sites More sharing options...
pilgrimvalley Posted July 12, 2021 Author Share Posted July 12, 2021 when you say the powerjack inverters has no surge protection? they just shut down due to overload or what have you observed? the battery charging from the solar panel is not an issue for me at this moment. i have a 400amp class t fuse between the inverters and the LiFePO4 batteries. two separate systems. i am on process of assembling a higher amp (1088 amp) LiFePO4 battery at 24-volts currently. is the issue when a heavy load starts and the surge amps are too high for the inverter? what problems have you encountered? Quote Link to comment Share on other sites More sharing options...
dickson Posted July 12, 2021 Share Posted July 12, 2021 when i complained and made a negative review they no longer allow me to bid on ebay Is that what ebay allow the seller do if negative review ? Other in this forum say they are also block in the US and from powerjack in China . Now I better not make any more review . Thank you . Quote Link to comment Share on other sites More sharing options...
Sid Genetry Solar Posted July 12, 2021 Share Posted July 12, 2021 54 minutes ago, pilgrimvalley said: is the issue when a heavy load starts and the surge amps are too high for the inverter? what problems have you encountered? If the surge amps are too high for the FETs, the inverter likely will blow up. No surge protection as in, there's no way to instantaneously shut down if a short-circuit condition is detected. 1 Quote Link to comment Share on other sites More sharing options...
dickson Posted July 12, 2021 Share Posted July 12, 2021 when you say the powerjack inverters has no surge protection? they just shut down due to overload or what have you observed? GS 6000 watt inverter has surge protection and will shut down at over 8000 watts . The 15kw PS will start my 4 ton heat pump because it do not know the 28000 watts surge because last only for less than a second and will start the heat pump no matter what . The 15kw now run 1 and 1/2 hour with Delta fans and will shut when temp reach 170 degree F but the voltage drop fast and the square wave cause me to manually shut down earlier . I let it cool down 2 hours because FETS is 135 degree F and will probably blow up all 24 FETS if I restart immediately . I do not want to be a guineypig . Quote Link to comment Share on other sites More sharing options...