Here's the basic output of a split-phase inverter and it's relation to the transformer design:

image.png.d21fa9843275fff4291d33b71becbd3f.png

You can ignore the Neutral line if you just want 240v single-phase.  With a GS inverter set up for split-phase output (standard), you shouldn't need a step up/down transformer--you can power 110/120v loads off of one phase (or the other).  220/240v loads can be powered off the total output.  And of course, you can adjust the output voltage between 110/120v per half phase (220/240 total output) from the settings.

  • Like 1
Link to comment
Share on other sites

24 minutes ago, ask first said:

So basically the European 220v is base solely of two 110v whereas the US 220/240v is tased of either two 110v or 120v?

Could be, though if the EU doesn't use 110v at all, their transformers will simply omit the center tap ("neutral").  U.S. runs most appliances on 120v, with larger appliances calling for 240v.

Link to comment
Share on other sites

On this site you can order one I think the specs are on here two

There is lots of videos on YouTube of sean testing and running  the GS 6k inverter

It will do 6k as long as the temp in room is at or below 100 degrees 

Sean runs one that had the safety limit turned of at 8k on a video 

He also started a window ac when already running 4or5k

  I am just a customer i happen to see your question 

You will like the GS inverter 

 

  • Like 1
Link to comment
Share on other sites

5 hours ago, ask first said:

Thank you there Ben. What is the safest wattage to run the say 6kw inverter? The power jack says 6kw surges at 12kw but continuous at 3kw. What is with these numbers?

 

 

Well, first of all...PJ ratings really don't mean anything.  GS inverters are tested to the listed ratings, and we know they are capable of handling the advertised load.

Link to comment
Share on other sites

31 minutes ago, ask first said:

Thanks Sid. I just watched your video from may 30th. I think I'll stick with the 80% rule you mentioned. Where are the specs listed for the genetry inverters?

Sean likes to run the 6kw inverter at redline for hours on end--and they handle it with aplomb.  6kw continuous 24/7 shouldn't be a problem. 

Surge is uncharacterized--actually, we're kinda looking to try to figure out just how much surge his 3 ton A/C unit pulls.  We know a single 6kw GS inverter starts it without hesitation, but I don't know what the absolute peak surge there is...

Link to comment
Share on other sites

3 hours ago, Sid Genetry Solar said:

Sean likes to run the 6kw inverter at redline for hours on end--and they handle it with aplomb.  6kw continuous 24/7 shouldn't be a problem. 

Surge is uncharacterized--actually, we're kinda looking to try to figure out just how much surge his 3 ton A/C unit pulls.  We know a single 6kw GS inverter starts it without hesitation, but I don't know what the absolute peak surge there is...

Enough serge to get your jollies off. I mean to be able to start a AC with 77A start up while running other stuff. thats crazy.  I bet his battery screams when it does that though.

Link to comment
Share on other sites

On 6/13/2021 at 11:19 PM, The Blind Wolf said:

Enough serge to get your jollies off. I mean to be able to start a AC with 77A start up while running other stuff. that's crazy.  I bet his battery screams when it does that though.

For the surge load, that is probably mostly down to the capacitors and the inductive properties of the big transformer in the GS inverter for the instantaneous load. That gives the battery enough time to react to the sag in voltage. 
 

That being said, if Sean had access to an oscilloscope current clamp probe it would be possible to take single shot tests and display the overall current being drawn in the first fractions of a second and even see how much if any ringing is present when the load starts.  That measurement is often not caught by regular clamp meters because they are not fast enough.  Some electric motors can surge over 7 times the running current to start but that surge may only be a fraction of a millisecond.  It would be interesting to see where the upper limit actually is on an unlocked GS inverter since you could then set a locked GS inverter at 1/4 to 1/3 that limit and know that you have plenty of surge capability without getting anywhere near the danger zone.  If I had to guess knowing that I have personally pulled over 4000 watts at 120v through the primary of a MOT with a custom wound secondary with a 1 second impulse. I would guess that the transformer and FETs in a GS inverter could safely handle a 20-25KW surge for a fraction of a second without issue but it is nice to see what it can do in a real world test.  Not that anyone should be pushing equipment beyond its rated 100% duty cycle.  Some day I need to buy a better bench scope and do some of my own tests on some of the household loads I have around so I can provide some more data to the community.

Link to comment
Share on other sites

47 minutes ago, kuhrd said:

That being said, if Sean had access to an oscilloscope current clamp probe it would be possible to take single shot tests and display the overall current being drawn in the first fractions of a second and even see how much if any ringing is present when the load starts.

Very good idea.  We can actually "borrow" a standard large-size PJ current transformer, and put it over the battery cable to a GS inverter...it'll give an AC representation of the current (no DC component), but I have calculated/figured out the scale on that, and it might be quite informative.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share

×
×
  • Create New...