Sean Genetry Solar Posted May 19, 2021 Share Posted May 19, 2021 This thread is for all the details of our new 'Split Sync' mode that we offer on all our GS inverters. This topic will be updated by myself and Sid with all relevant info pertaining this new mode. In basic terms, the Split Sync mode allows you to run 2 inverters together that will share the load of a 240V service panel. It is similar to daisy chain but is a preferred method when running just 2 inverters. It allows you to double your surge and load capabilities assuming you have a well balanced service panel. Each inverter acts like a Single L coming into the panel and they operate 180 degrees out of phase from each other. There is a downside to this mode. If you have purchased a GS inverter you will need to send it in (or do yourself by breaking warranty) because the inverter needs to be rewired for 120V regardless of if you chose to have 120v inputs. If your plan is to run in split mode and you have not purchased an inverter then it can be setup here. Another Downside is you can only run with 2 inverters. So if you plan to have 3 or more inverters then this mode would not work for you and daisy mode would be the only option. The picture below shows 2 inverters setup for Split Sync mode. S = Slave Inverter (Inverter must be set to "Split Sync Slave" in the LCD) M = Master Inverter (Set as Normal) N = Neutral E = Signal Patch L1 = Line 1 L2 = Line 2 NN + NN are tied together between the 2 units. E + E are tied together between the 2 units. M L1 + S E L2 + L2 are NOT tied between the 2 units but rather tied together at the inverter to give full output L1 + L1 are NOT tied between the 2 units but rather tied together at the inverter to give full output N + N are tied together between the 2 units. Your L1, L2, N would lead to the breaker panel in much the same way a 240V Split phase inverter would. Quote Link to comment Share on other sites More sharing options...
Sid Genetry Solar Posted May 19, 2021 Share Posted May 19, 2021 Edit by Sean : Fixed the OP to reflect the correct info. EDIT: "E" "E" as pictured do NOT get tied together. "E" is the input AC signal line. For the master inverter, you can either connect this to a generator input (120v only), OR you can put the master inverter in "master split-sync mode", and connect this input to the "L" output of the slave inverter. In this setup, the master inverter will shut down if it detects the loss of a feedback signal (i.e. "slave" inverter shut down for whatever reason.) For the "slave" inverter, this "E" terminal goes to the "L" output of the master inverter; this is the sync input signal, which the "slave" offsets by 180 degrees. Quote Link to comment Share on other sites More sharing options...
The Blind Wolf Posted May 19, 2021 Share Posted May 19, 2021 1 hour ago, Sid Genetry Solar said: EDIT: "E" "E" as pictured do NOT get tied together. "E" is the input AC signal line. For the master inverter, you can either connect this to a generator input (120v only), OR you can put the master inverter in "master split-sync mode", where it will shut down if it detects the loss of a feedback signal (i.e. "slave" inverter shut down for whatever reason.) For the "slave" inverter, this has to go to the "L" output of the master inverter; this is the sync input signal, which the "slave" offsets by 180 degrees. Oy. confusing much. . . Sean post really thrown me for a loop. . . and Sid yours just did too. Quote Link to comment Share on other sites More sharing options...
dickson Posted May 19, 2021 Share Posted May 19, 2021 EDIT: "E" "E" as pictured do NOT get tied together. "E" is the input AC signal line. Please show photo of the 2 GS 120vac inverters wired as split sync mode . Quote Link to comment Share on other sites More sharing options...
Sid Genetry Solar Posted May 19, 2021 Share Posted May 19, 2021 Here's the best I have for that. Notice that there are 2 "L" and 2 "N" outputs for each inverter, this paralleling is necessary for the 50A total at max load. Wires are rated for the 25A max load @ 240v, so when we go to single-phase, the full output load at 120v is 50A. Sync wire is the green one; that provides the "sync" signal to the slave inverter to follow. The unused terminal on the "master" inverter is the 120vAC input. EDIT: Just realized this is an older photo without the stickers. Master inverter is on the right, slave inverter is on the left. Quote Link to comment Share on other sites More sharing options...
dickson Posted May 19, 2021 Share Posted May 19, 2021 Slave always label L2 and master always label L1 . E on slave always go to L1 on master . L1 on slave go to breaker panel and L2 on master go to breaker panel and one neutral wire from either slave or master go to breaker panel . Never connect E from master to L2 or bad thing will happen I think . Thank you . Quote Link to comment Share on other sites More sharing options...
Sean Genetry Solar Posted May 19, 2021 Author Share Posted May 19, 2021 58 minutes ago, The Blind Wolf said: Oy. confusing much. . . Sean post really thrown me for a loop. . . and Sid yours just did too. Sorry I put the sticker in the wrong spot and neither Sid nor I noticed till this post. It is correct on the video though. Quote Link to comment Share on other sites More sharing options...
Sean Genetry Solar Posted May 19, 2021 Author Share Posted May 19, 2021 1 hour ago, dickson said: EDIT: "E" "E" as pictured do NOT get tied together. "E" is the input AC signal line. Please show photo of the 2 GS 120vac inverters wired as split sync mode . Corrected the photo above Quote Link to comment Share on other sites More sharing options...
Sid Genetry Solar Posted May 19, 2021 Share Posted May 19, 2021 24 minutes ago, dickson said: Never connect E from master to L2 or bad thing will happen I think You can connect E from master to L2 (slave L) if the master is configured for "master split-sync" mode, in which case the signal becomes a "stay on" signal. (If it's in Normal mode, it'll really get confused trying to sync to this 180-degree offset wave.) Quote Link to comment Share on other sites More sharing options...
dickson Posted May 19, 2021 Share Posted May 19, 2021 "master split-sync" mode, in which case the signal becomes a "stay on" signal. Many different programs in wifi board and need to be careful . Thank you . Quote Link to comment Share on other sites More sharing options...
The Blind Wolf Posted May 19, 2021 Share Posted May 19, 2021 (edited) When you do your Manual. . . *cough* Might want to make sure you have a big clear with correct wire color picture for those who can't read. . . And Correct Wording for those who follow everything to the letter. . . *Evil Grin* Also, I would personily change the E to a S for the letter Sense wire. or SW if you going to slap a sticker on the terminal to indacate this. Not Many going to know what E is. Edited May 19, 2021 by The Blind Wolf Quote Link to comment Share on other sites More sharing options...
Sid Genetry Solar Posted May 19, 2021 Share Posted May 19, 2021 Yeah, when.... Currently loading up a PCB manufacturer's cart with 9 separate PCB designs that need prototyped before sending them off to production... ...oh, and revising a few of the designs while I'm at it. Quote Link to comment Share on other sites More sharing options...
The Blind Wolf Posted May 19, 2021 Share Posted May 19, 2021 55 minutes ago, Sid Genetry Solar said: Yeah, when.... Currently loading up a PCB manufacturer's cart with 9 separate PCB designs that need prototyped before sending them off to production... ...oh, and revising a few of the designs while I'm at it. 9 pcbs? all gs related or other new hush, hush products. . . Quote Link to comment Share on other sites More sharing options...
Sean Genetry Solar Posted May 20, 2021 Author Share Posted May 20, 2021 11 hours ago, The Blind Wolf said: When you do your Manual. . . *cough* Might want to make sure you have a big clear with correct wire color picture for those who can't read. . . And Correct Wording for those who follow everything to the letter. . . *Evil Grin* Also, I would personily change the E to a S for the letter Sense wire. or SW if you going to slap a sticker on the terminal to indacate this. Not Many going to know what E is. The stickers were for you only basically to help your electrician hook it up. I used some old power jack stickers I had laying around to label everything for you. I did not have a big letter S in the sticker pack. For everyone else they will need to read the manual since I don't want to put stickers all over our inverters and turn them into power jack. E to me is like Equipment. Quote Link to comment Share on other sites More sharing options...
The Blind Wolf Posted May 20, 2021 Share Posted May 20, 2021 Ah. Well E still could mean Earth Ground too. like Equipment ground. Not sure how hard it would be, maybe on the next order, have some plates made with the split phase lettering setup on it and one wit the normal, and you can just change out the plate when somebody orders it that way. The inverts are out for delivery right now by the way. Quote Link to comment Share on other sites More sharing options...
Sean Genetry Solar Posted May 26, 2021 Author Share Posted May 26, 2021 OP has been updated with Video Demonstration Quote Link to comment Share on other sites More sharing options...